Thermostat?
-
- 1 star
- Posts: 1
- Joined: Sat 25 Feb 2012, 17:16
Thermostat?
Could someone help how to make a Thermostat? So when my datasource (weather station indoor temp) go under 5 celcius device go on. when it rises abobe 5.3 it turn device off. 

-
- Administrator
- Posts: 2655
- Joined: Tue 09 Nov 2010, 20:25
Re: Thermostat?
The key here is "hysteresis"...
Create a group schedule linked to a rule, where the group schedule is set to be turned on at 00:00.
Specify that the rule is fulfilled when the temperature (collected from an existing data source) is less than 5 degrees, with a hysteresis of 0.3 degrees. This means that when the temperature drops between 5 degrees, the device will be turned on.
It will stay on until the temperature reaches 5.3 degrees.
Create a group schedule linked to a rule, where the group schedule is set to be turned on at 00:00.
Specify that the rule is fulfilled when the temperature (collected from an existing data source) is less than 5 degrees, with a hysteresis of 0.3 degrees. This means that when the temperature drops between 5 degrees, the device will be turned on.
It will stay on until the temperature reaches 5.3 degrees.
Martin | Switch King
-
- 1 star
- Posts: 9
- Joined: Sun 20 May 2012, 11:49
Re: Thermostat?
Hi,
I have the same quesion but for two differents periods.
I would like to have 18°C-19°C from 6 AM to 23 PM and 15°C-16°C from 23 PM to 6 AM the day after. What should i do ?
Two shedules (resp. On at 6AM-Off at 23PM and On at 23PM-Off at 6AM) don't work.
thanks,
I have the same quesion but for two differents periods.
I would like to have 18°C-19°C from 6 AM to 23 PM and 15°C-16°C from 23 PM to 6 AM the day after. What should i do ?
Two shedules (resp. On at 6AM-Off at 23PM and On at 23PM-Off at 6AM) don't work.
thanks,
-
- Administrator
- Posts: 2655
- Joined: Tue 09 Nov 2010, 20:25
Re: Thermostat?
This should work, but the server might think that since you have contradictory actions at the exact same time - i.e. both an On and an Off at 6AM, Switch King might have problems with these entries due to that they would take each other out.
You will probably see a warning message regarding this in Switch Kings log file.
If you make the schedules overlap - i.e. one schedule turns on at 06:00 and one off at 06:01, you might get around this.
You will probably see a warning message regarding this in Switch Kings log file.
If you make the schedules overlap - i.e. one schedule turns on at 06:00 and one off at 06:01, you might get around this.
Martin | Switch King
-
- 1 star
- Posts: 9
- Joined: Sun 20 May 2012, 11:49
Re: Thermostat?
I have fixed the problem as you described. I let a few minutes between two commands and that works perfectly.
Thanks !
regards,
Thanks !
regards,